W wyboy Senior Member Apr 21, 2010 #1 Do steel chase nipples meet the requirement of NEC 259.97 for bonding over 250 volts
jumper Senior Member Location 3 Hr 2 Min from Winged Horses Apr 21, 2010 #2 For what type of enclosure and what type of knockouts?
W wyboy Senior Member Apr 21, 2010 #3 gutter with a punched gutter with a punched From a gutter with a punched KO to an enclosure with a punched KO.
gutter with a punched gutter with a punched From a gutter with a punched KO to an enclosure with a punched KO.
jumper Senior Member Location 3 Hr 2 Min from Winged Horses Apr 21, 2010 #4 wyboy said: From a gutter with a punched KO to an enclosure with a punched KO. Click to expand... I am probably wrong, but I say yes. It seems to meet exception (3).
wyboy said: From a gutter with a punched KO to an enclosure with a punched KO. Click to expand... I am probably wrong, but I say yes. It seems to meet exception (3).
raider1 Senior Member Staff member Location Logan, Utah Apr 21, 2010 #5 jumper said: I am probably wrong, but I say yes. It seems to meet exception (3). Click to expand... I agree, a chase nipple would meet the exception condition #3. Chris