I'm in a debate with an electrician who's responsible for installing a fire detection system that our company designed. Our contract is with the end user and this equipment was free issued to the electrician, so I have no contractual relationship with them.
Our drawings don't show an installation detail for the installation of a smoke detector on a suspended ceiling tile because we assumed the electrician would install it correctly. He's disagreeing with me. I'm getting ready to state my position and wanted to make sure I was correct and wasn't missing anything.
Chapter 3 of the NEC (2005 edition) addresses “Wiring Methods and Materials”. Section 300.11 addresses “Securing and Supporting” and states:
1 - Use a "T-Bar" hanger to span between the grid.
2 - Attach the junction box to the "T-Bar" hanger.
3 - Run a support wire from the junction box to the structure above the ceiling tile.
If I'm interpreting 300.11 incorrectly, or should be referencing some other section of the code please let me know.
What 300.11 isn't telling me, and I can't find the reference for, is that I can't Sandwich the ceiling tile between the junction box and the smoke detector base...correct? What's the code reference?
Any help is appreciated
Our drawings don't show an installation detail for the installation of a smoke detector on a suspended ceiling tile because we assumed the electrician would install it correctly. He's disagreeing with me. I'm getting ready to state my position and wanted to make sure I was correct and wasn't missing anything.
Chapter 3 of the NEC (2005 edition) addresses “Wiring Methods and Materials”. Section 300.11 addresses “Securing and Supporting” and states:
(A) Securing in Place. Raceways, cable assemblies, boxes cabinets, and fittings shall be securely fastened in place. Support wires that do not provide secure support shall not be permitted as the sole support. Support wires and associated fittings that provide secure support and that are installed in addition to the ceiling grid support wires shall be permitted as the sole support. Where independent support wires are used, they shall be secured at both ends. Cables and raceways shall not be supported by ceiling grids
To my mind, this means that if I install a smoke detector on a suspended ceiling I must:1 - Use a "T-Bar" hanger to span between the grid.
2 - Attach the junction box to the "T-Bar" hanger.
3 - Run a support wire from the junction box to the structure above the ceiling tile.
If I'm interpreting 300.11 incorrectly, or should be referencing some other section of the code please let me know.
What 300.11 isn't telling me, and I can't find the reference for, is that I can't Sandwich the ceiling tile between the junction box and the smoke detector base...correct? What's the code reference?
Any help is appreciated