NEC 300.15.(f)

Merry Christmas

corison

New User
Location
Las Vegas
Occupation
Journeyman Electrician
I feel like this section gives me permission to use a transition fitting as a pull point. We often use a short piece of flex or seal tight to create an expansion joint in a non flexible pipe run. Im wondering if this section could be interpreted to allow these listed transition fittings to be used as pull points? Thoughts?
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
You would not be using the transition fitting as a pull point. The transition fitting makes the connection between the flexible conduit and the non-flexible conduit.
While disconnecting the flex to pull the cable is common, it is a technical violation of 300.18(A).
 