While working for an electrical contractor, I noticed the foreman directing his journeyman to install FMC; install the conductors; then install and terminate luminaires that will finally be installed in an inaccessible ceiling.
The FMC was left long, and when the ceiling grid was installed, the electricians basically curled up the FMC and completed the fixture installation.
I had a problem with this, citing 300.18(A) as this was not "installed complete" as per the said article. I've run into this in the past, so I rattled off the article off the top of my head. However, when I read 300.18 again to refresh my memory, I realized the article also included: "Where required to facilitate the installation of utilization equipment, the raceway shall be permitted to be initially installed without a terminating connection at the equipment".
I then read the Article 100 definition of Utilization Equipment, and to my surprise is the word ''lighting''.
Although I believe my initial citation is correct, what argument would I have with regards to the NEC? I also fall back on Article 348.22 (as well as other raceway systems) regarding the 360 degree bend rule.
Any comments would be greatly appreciated. Thank you.