I recently ran accross a single family dwelling installation where the electrician had a 6/2 WG ran to a 240V sub panel for a spa. After the arrival of the spa it was determined a neutral was required. So the electrician added a #10 THWN from the service panel, through the attic, to the sub panel. Clearly this is more than 1 specific violation and not the basis for this question.
The question is, with the neutral conductor being seperate from the phase conductors, and of different characteristics, what would be the specific reasons for premature failure of the electronic circuit board in the spa? I suspect the board mounted transformer is a 120V primary but have not confirmed this.
I have seen before on a 3 phase lighting circuit where only two of the phase conductors were brought down each row, caused the ballasts to prematurly fail. When the installation was changed to include all of the branch circuit conductors in the same raceway, the ballasts functioned normally.
The question is, with the neutral conductor being seperate from the phase conductors, and of different characteristics, what would be the specific reasons for premature failure of the electronic circuit board in the spa? I suspect the board mounted transformer is a 120V primary but have not confirmed this.
I have seen before on a 3 phase lighting circuit where only two of the phase conductors were brought down each row, caused the ballasts to prematurly fail. When the installation was changed to include all of the branch circuit conductors in the same raceway, the ballasts functioned normally.