DetroitEE
Senior Member
- Location
- Detroit, MI
We are designing power feeds to a busway, which powers a moving machine that is on electrified rails. It has been requested that we feed the busway at multiple points with the same circuit; the reasoning is that the total length of the busway is long, and the electrified bus itself is small due to physical constraints, and therefore voltage drop would be an issue if the machine were at the far end of the track and it were only fed at one location. The busway is electrically continuous for the whole length, there are no breaks. The theory is that if we use larger conductors, run along side the busway and then connected to the busway every 10-20', this would solve the voltage drop issue.
I'm trying to determine if this type of installation is even permissible per the NEC. My first thought was that this would be a violation of 310.10(H)(1) as we would have paralleled conductors of different lengths (definition of paralleled is "electrically joined at both ends"). The current would divide itself among all of the different busway taps, proportional to the impedance. This unequal division of current among the circuit conductors seems to be just what the paralleling rules seem be prohibiting.
Any feedback or thoughts would be appreciated.
I'm trying to determine if this type of installation is even permissible per the NEC. My first thought was that this would be a violation of 310.10(H)(1) as we would have paralleled conductors of different lengths (definition of paralleled is "electrically joined at both ends"). The current would divide itself among all of the different busway taps, proportional to the impedance. This unequal division of current among the circuit conductors seems to be just what the paralleling rules seem be prohibiting.
Any feedback or thoughts would be appreciated.