310.1 (Scope) says in part "These requirements do not apply to . . . conductors specifically provided for elsewhere in this Code."
310.4 says "Insulated conductors shall comply with Table 310.4(A) and Table 310.4(B)," but the inner conductors in NM cable don't match any of the entries in Table 310.4(A). Indeed 334.112 says "The insulated power conductors shall be one of the types listed in Table 310.4(A) that are suitable for branch-circuit wiring or one that is identified for use in these cables." The listing standard for NM cable identifies the insulation used on the power conductors in lieu of complying with Table 310.4(A).
310.8(A) says "All conductors and cables shall be marked to indicate the following information, using the applicable method described in 310.8(B):" But NM cable inner conductors are not marked and so don't comply with 310.8(A).
My conclusion is that NM cable inner conductors only comply with Article 310 via the exclusion in the scope in 310.1 for "conductors specifically provided for elsewhere in this Code," in this case provided for by Article 334. That scope exclusion waives all requirements in Article 310.
Therefore NM cable inner conductors are not subject to 310.10(H) on parallel conductors, and it is OK to parallel NM cable inner conductors in any size.
Comments? : - )
Cheers, Wayne
310.4 says "Insulated conductors shall comply with Table 310.4(A) and Table 310.4(B)," but the inner conductors in NM cable don't match any of the entries in Table 310.4(A). Indeed 334.112 says "The insulated power conductors shall be one of the types listed in Table 310.4(A) that are suitable for branch-circuit wiring or one that is identified for use in these cables." The listing standard for NM cable identifies the insulation used on the power conductors in lieu of complying with Table 310.4(A).
310.8(A) says "All conductors and cables shall be marked to indicate the following information, using the applicable method described in 310.8(B):" But NM cable inner conductors are not marked and so don't comply with 310.8(A).
My conclusion is that NM cable inner conductors only comply with Article 310 via the exclusion in the scope in 310.1 for "conductors specifically provided for elsewhere in this Code," in this case provided for by Article 334. That scope exclusion waives all requirements in Article 310.
Therefore NM cable inner conductors are not subject to 310.10(H) on parallel conductors, and it is OK to parallel NM cable inner conductors in any size.
Comments? : - )