dselgra1
Member
- Location
- Des Moines, IA
So my question is if you are using 4 wire 3phase and considering your neutral a current carry device per 310(B)(4)(c) 2008 per 310 (B)(2)(a) you would have to derate to 80% your wire. If you are already using an 80% rated breaker doesn't this already make the wire 80% rated. It seems ridiculous to example: 200A 4 wire 3 phase service with a 200A 80% rated MCB making the max load going through the conductor 160A and if you have to derate the conductor 80% per above a 250A conductor that there is 90A wasted.