Can someone help me please.
nec 312.8.. you should not used enclosures/panelboards as junction boxes or raceways for conductors feeding trough or tapping off ...Unless adequate space for this purpose is provided.
The conductors shall not fill the wiring space at any cross section to more than 40 % of the cross-sectional area of the space,
and the conductors, splices, and taps shall not fill the wiring space at any cross section to more than 75% of the cross-sectional area of that space.
Do you deduct the space taken by existing swithes/ovecurrent devices and than take 40/75%?
Or you calculate the whole enclosure/panelboard including everything?
nec 312.8.. you should not used enclosures/panelboards as junction boxes or raceways for conductors feeding trough or tapping off ...Unless adequate space for this purpose is provided.
The conductors shall not fill the wiring space at any cross section to more than 40 % of the cross-sectional area of the space,
and the conductors, splices, and taps shall not fill the wiring space at any cross section to more than 75% of the cross-sectional area of that space.
Do you deduct the space taken by existing swithes/ovecurrent devices and than take 40/75%?
Or you calculate the whole enclosure/panelboard including everything?