Hello All, first time here, so thanks in advance!
Per 2020 NEC 314.16, what is the minimum Underwater Junction Box (JB) volume? I have looked at all the Tables and read the text; I need to confirm I'm doing this correctly. I tried to insert an image, but for some reason, that does not work.
There are three #12 conductors coming from the Control Panel (CP) to the JB.
Six underwater LEDs are connecting to the JB.
Each underwater LED has three #18 conductors for a total of eighteen #18 conductors.
Each one of the #12 conductors will connect to six #18 conductors.
12 * 36.9 = 110.7 cm3
18 * 24.6 = 442.8 cm3
Total = 553.5 cm3
Per 2020 NEC 314.16, what is the minimum Underwater Junction Box (JB) volume? I have looked at all the Tables and read the text; I need to confirm I'm doing this correctly. I tried to insert an image, but for some reason, that does not work.