bdm5066
Member
- Location
- Pittsburgh, PA
I am sizing a manhole for pulling medium voltage cable (shielded in this case).
314.71(A) provides requirements for straight pulls -> 48* largest cable diameter
314.71(B) provides requirements for angle pulls. -> 36* largest cable diameter + the sum of all other cable diameters
What I'm struggling with is how to calculate the manhole size for an application with both straight and angle pulls. If 10 conduits worth of cable are angled and 5 are straight, can I do the following
36*largest cable diameter + sum of all other cable diameters in the 10 conduits
or do I need to do the following:
36*largest cable diameter + sum of all other cable diameter in the 15 conduits
In my application, both of the above calculations result in larger manhole sizes than the straight pull formula.