- Location
- Roanoke, VA
- Occupation
- Retired Electrical Engineer, Teacher
Greetings. I have read a previous post on the reason for NEC 344.14 requiring only stainless steel fittings on stainless steel RMC. None of the responses address the following situation: on certain secure facilities we would use RMC as a tamper-resistant carrier, then put in a dielectric brake - simply a Schedule 80 PVC adapter - then resume RMC when traversing certain boundaries.
Supposing the RMC is stainless, why is this not permissible by 344.14? It makes sense to prohibit dissimilar metal fittings, but what about PVC? No galvanic action possible. In fact, 344.14 is titled: Dissimilar Metals. But then it says:
"Stainless steel rigid conduit shall only be used with the following:
(1) Stainless steel fittings"
And no exception for nonmetallic fittings.
I'm brand new to the forum and somewhat new to the NEC, so I apologize if there is some other thread or NEC clause I missed concerning this.
Supposing the RMC is stainless, why is this not permissible by 344.14? It makes sense to prohibit dissimilar metal fittings, but what about PVC? No galvanic action possible. In fact, 344.14 is titled: Dissimilar Metals. But then it says:
"Stainless steel rigid conduit shall only be used with the following:
(1) Stainless steel fittings"
And no exception for nonmetallic fittings.
I'm brand new to the forum and somewhat new to the NEC, so I apologize if there is some other thread or NEC clause I missed concerning this.