8- 219 - (345-11, 346-11): Reject
SUBMITTER:
Bruce Mitchell, Thornton, CO
RECOMMENDATION
Revise text to read as follows:
The cumulative total of all angles formed by bending of the
conduit between pull points (e.g. conduit bodies and boxes) shall
not exceed 360?.
SUBSTANTIATION:
Current language is imprecise and could be
interpreted as implying that any bend greater than a quarter (90?) is
not allowed.
PANEL ACTION:
Reject.
PANEL STATEMENT:
The existing text adequately explains the
requirements for conduit bends. Four quarter bends is used as an
example and does not limit the angle of any bend to 90 degrees or
less.
NUMBER OF PANEL MEMBERS ELIGIBLE TO VOTE:
14
VOTE ON PANEL ACTION:
AFFIRMATIVE: 13
NOT RETURNED: 1 Corry