Two Questions related to, NEC 392.80(A)(2)a;
Does the code expect an additional deduction of ambient temperature for conductor amp capability?
My example:
-given:
a. single conductor in open cable tray: 300CU = 500amps from T310.15(B)(17);
b. ambient temperature derate of .91 for average high temperature of 100 degree F from T310.15(B)(2)(A)
c. derate for open cable tray with single conductor of .65 from NEC 392.80(A)(2).
d. no issues with cable tray width or space.
Result: 500A x .91 x.65 = 295 amps
Makes sense to include derate for ambient by area, If this is the case should the code add this requirement?