KarlS
Member
- Location
- Houston, TX
I ran 500MCM cables - 2 per phase triplexed per NEC 392 with min 2.15 x OD. This section states to use 310.20 for tray cable. The cables are between copper bus connections on switchgear power breakers at 800at and MLO connections on 480V motor control centers. per table 310.20, I can use the 90C column due to copper bar connections on both SWGR and MCC. Based on this, my designer over sized the cables at 500MCM. I could go with 2-300MCM per phase at 90C. Here is the trouble. I have a customer that states due to NEC 110.14 C 1 - I must use 310.16 to size these cables.
I have had customers point out this section before for cable connections to breakers. Stating I must use 310.16 and the 60C column to size my cables. Molded case breakers are marked for use with 75C.
My lugs are rated 90C.
I think NEC 392 is correct. We have used this for years to size tray cable.
I have had customers point out this section before for cable connections to breakers. Stating I must use 310.16 and the 60C column to size my cables. Molded case breakers are marked for use with 75C.
My lugs are rated 90C.
I think NEC 392 is correct. We have used this for years to size tray cable.