A Alex at Spinnaker New member Jan 20, 2011 #1 are multi family properties required to compliy wit hthis rule in WA state, or only treatment facilties as outlined in WAC 246-337-140?
are multi family properties required to compliy wit hthis rule in WA state, or only treatment facilties as outlined in WAC 246-337-140?
B Bea Senior Member Jan 23, 2011 #2 406.11 would apply to mulitfamily dwelling units and units that have the features of dwelling unit as defined atricle 100 of the nec.
406.11 would apply to mulitfamily dwelling units and units that have the features of dwelling unit as defined atricle 100 of the nec.
tom baker First Chief Moderator & NEC Expert Staff member Location Bremerton, Washington Occupation Master Electrician Jan 23, 2011 #3 There is no exception in Washington Electrical Rules chapter 206-46B for TR receptacles, so any rule in the 2008 NEC applies, as the above post stated, if its a dwelling unit this rule applies.
There is no exception in Washington Electrical Rules chapter 206-46B for TR receptacles, so any rule in the 2008 NEC applies, as the above post stated, if its a dwelling unit this rule applies.