NEC 408.3(C) Switchboard section bonding

Status
Not open for further replies.

rojay

Senior Member
Location
Chicago,IL USA
What does compliance with the last part of NEC 408.3(C) require? Does a bonding jumper need to be daisy chained between the ground bus of each switchboard section?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Doesn't each section have a piece of factory supplied bus to connect the EGC bus together from section to section?
 

rojay

Senior Member
Location
Chicago,IL USA
Doesn't each section have a piece of factory supplied bus to connect the EGC bus together from section to section?
Yes, there is. That’s exactly what is prompting my question. It seems like the code is requiring a redundant connection? I’ve never done or seen anyone do this before.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Yes, there is. That’s exactly what is prompting my question. It seems like the code is requiring a redundant connection? I’ve never done or seen anyone do this before.
No a redundant connection is not required. The factory supplied bus jumper is a bonding jumper.
 