Nec 408.36(c)

Status
Not open for further replies.

erickench

Senior Member
Location
Brooklyn, NY
This is something that I noticed over 10 years ago. The above NEC section states:

Panelboards equipped with snap switches rated at 30 amperes or less shall have overcurrent protection of 200 amperes or less.

Can anyway give me an example of an installation that has 30A snap switches inside a panelboard with the main protection being as high as 200A? I always thought that circuit breakers were used for branch circuits inside panelboards.
 
Some old fuse panels had switches inline before the fuses. You would turn the switch off before changing the fuse.

I am going to be at a church tonight that has one of these in the room we meet at. I'll snap a picture and post it tonight or tomorrow.
 
This is something that I noticed over 10 years ago. The above NEC section states:

Panelboards equipped with snap switches rated at 30 amperes or less shall have overcurrent protection of 200 amperes or less.

Can anyway give me an example of an installation that has 30A snap switches inside a panelboard with the main protection being as high as 200A? I always thought that circuit breakers were used for branch circuits inside panelboards.


I think that section has changed a bit in 08.
I thought it had to do with single pole breakers installed with out a main.
Such as 4 double pole breakers and 2 single poles being used as six disconnects.
 
As promised -

HPIM0985.jpg


HPIM0983.jpg
 
Thanks for the pictures. How was church? Monday too, must have been revival or a decons meeting.
I did see a couple 30's in there. They must go to the coffee pot, etc...



Hey Dennis didn't this article change in the 08 code. I can't find the one described above in the 08 book.
 
You've all been very helpful with the pictures. I came across this in the '90s when I was still doing construction inspection. I was trying to solve a problem. Wish I could remember what the problem was.
 
Tell me. Does anyone know if these type of installations are still used in construction? It seems that these snap switches are unprotected. They are rated at 30A but the fuses are allowed to be as high as 200A.:confused:
 