Here is what Eaton says on their website:
According to NEC 408.36(D) Plug-in-type overcurrent protection devices or
plug-in type main lug assemblies that are back-fed and used to terminate
field-installed ungrounded supply conductors shall be secured in place by
an additional fastener that requires other than a pull to release the device
from the mounting means on the panel. "Field-installed" is the key, if we as
the manufacturer use a back-fed breaker or main lug assembly in a panel a
hold-down kit is not necessary. If a customer back-feeds a plug-in breaker
or main lug assembly that they field install a hold-down kit is required.
So: If I do a lineside tap do I have to add a holddown?
If I replace the breaker in kind after a failure do I have to add a holddown?
If it change the breaker size (presently 100A breaker on a 125A solar ready panel
Will use the Enphase Transfer switch to integrate the battery and PV into the system to no
PV or Batt to the MSP. ) to 125A and do the line side tap to insert the Transfer switch
between the meter and the main do I have to add the holddown?
Seems to confusing to me.
Tnx
T3
According to NEC 408.36(D) Plug-in-type overcurrent protection devices or
plug-in type main lug assemblies that are back-fed and used to terminate
field-installed ungrounded supply conductors shall be secured in place by
an additional fastener that requires other than a pull to release the device
from the mounting means on the panel. "Field-installed" is the key, if we as
the manufacturer use a back-fed breaker or main lug assembly in a panel a
hold-down kit is not necessary. If a customer back-feeds a plug-in breaker
or main lug assembly that they field install a hold-down kit is required.
So: If I do a lineside tap do I have to add a holddown?
If I replace the breaker in kind after a failure do I have to add a holddown?
If it change the breaker size (presently 100A breaker on a 125A solar ready panel
Will use the Enphase Transfer switch to integrate the battery and PV into the system to no
PV or Batt to the MSP. ) to 125A and do the line side tap to insert the Transfer switch
between the meter and the main do I have to add the holddown?
Seems to confusing to me.
Tnx