I haven't had any experience with the 84 circuit panelboards. In review of the 2008 & 2011 NEC (section 408.36), I am wondering if there is a possible typo or am I reading things wrong.
To paraphrase: The exception #2 states that individual protection shall not be required for a pnlbd protected on it's supply side by two mcb's or two sets of fuses having a combined rating not greater than that of the pnlbd. A pnbld wired under this exception must have no more than 42 ckts....
Am I to assume that by individual protection the code is inferring to a main ckt brkr located within the pnlbd itself? And, if so, what about an example of a 800A service utilizing the (6) handle rule with (6) 200A main brkrs serving (6) separate 42 ckt MLO panels. If I am reading this article correctly, this would not be an acceptable installation because there wouldn't be two breakers ahead of each panel. I'm thinking there was a typo that left out the previous (NEC 2005) reference of ... "not more than" two mcb's or two sets of fuses.... from the earlier edition of 408.36.
Thx to all for comments and input.
I'm a bit confused here and would appreciate any comments.