Jpflex
Electrician big leagues
- Location
- Victorville
- Occupation
- Electrician commercial and residential
A while back i asked a similar question here but the response was that "it was not code compliant."
What i was asking is wether a 14 AWG romex nm cable could be tapped from a 12 AWG romex nm cable within a junction box to supply power to standard incadecent light(s). I was told i could not.
However, I came across NEC 410.117 (C) that says a tap conductor with insulation suitable for the temperature encounteted [at the luminair] shall be permitted to to run from the luminair to an outlet box atleast 1 foot from the luminaire.
The conductirs nust be type ac or mc atleast 18" inches (contradicts previous 1 foot minimum rule unless bent?) But not over 6 feet
So it appears you can tap white romex from yellow romex unless exceeding a run of 6 feet?
What i was asking is wether a 14 AWG romex nm cable could be tapped from a 12 AWG romex nm cable within a junction box to supply power to standard incadecent light(s). I was told i could not.
However, I came across NEC 410.117 (C) that says a tap conductor with insulation suitable for the temperature encounteted [at the luminair] shall be permitted to to run from the luminair to an outlet box atleast 1 foot from the luminaire.
The conductirs nust be type ac or mc atleast 18" inches (contradicts previous 1 foot minimum rule unless bent?) But not over 6 feet
So it appears you can tap white romex from yellow romex unless exceeding a run of 6 feet?