From the statement below, how do you interpret the code? If the machine is located outdoor, and is dispensing tickets for customers, does NEC 422.51 applied or the code only apply for dispensing bigger thing?
What I am thinking is the incoming power 120A 30A Circuit should has an inline GFCI from the machine directly. Am i correct on that assumption? The circuit has it device ground tied to a grounding system on the ground and circuit ground as well
NEC 422.51
Cord-and Plug-Connected.Cord-and plug-connected vending machines manufactured or remanufactured on or after January 1, 2005, shall include a ground-fault circuit interrupter identified for portable use as an integral part of the attachment plug or be located within 300 mm (12 in.) of
the attachment plug. Older vending machines manufactured or remanufactured prior to January 1, 2005, shall be connected to a GFCI-protected outlet.
(B) Other Than Cord-and Plug-Connected.Vending machines not utilizing a cord and plug connection shall be connected to a ground-fault circuit-interrupter protected circuit
What I am thinking is the incoming power 120A 30A Circuit should has an inline GFCI from the machine directly. Am i correct on that assumption? The circuit has it device ground tied to a grounding system on the ground and circuit ground as well
NEC 422.51
Cord-and Plug-Connected.Cord-and plug-connected vending machines manufactured or remanufactured on or after January 1, 2005, shall include a ground-fault circuit interrupter identified for portable use as an integral part of the attachment plug or be located within 300 mm (12 in.) of
the attachment plug. Older vending machines manufactured or remanufactured prior to January 1, 2005, shall be connected to a GFCI-protected outlet.
(B) Other Than Cord-and Plug-Connected.Vending machines not utilizing a cord and plug connection shall be connected to a ground-fault circuit-interrupter protected circuit