I have a 3MVA, 3-phase transformer, with a 480V secondary from which I am using a 4000A, 100 percent rated breaker set to 3600A for switchgear main. I'm thinking NEC 430.24 should apply, but there is no exception for the 100% breaker rating.
If I calculate the load based strictly on this code section, I am in excess of 3600A, but if I base it on 100 percent of continuous, non continuous, and motor load plus 25% of largest motor, I'm fine. I think I'm using the right calculation, but is there a section that confirms it?