NEC 430.24 for packaged units

Status
Not open for further replies.
Location
CA, USA
The code says that the conductors must be sized with ampacity not less than the sum of 125% of the FLA rating of the highest rated motor and 100% of every other motor.

Let's say I have a packaged unit with (6) motors of identical sizes at each 15HP. This unit has a nameplate FLA.

Do I calculate the conductor with the nameplate FLA and 25% of that whole unit, or do I calculate the nameplate FLA with 25% extra of ONE single 15HP motor?

If possible can you provide code references?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
IMO if the package unit doesn't have a specific MCA and MaxOCPD specified then you calculate according to 125% of the largest motor + 100% of all of the others.
 
Location
CA, USA
IMO if the package unit doesn't have a specific MCA and MaxOCPD specified then you calculate according to 125% of the largest motor + 100% of all of the others.

Got it. They do not have those numbers yet, as the manufacturer is still designing it. We are trying to provide a ROM for pricing and don't want to be out of the hunt due to incorrectly oversizing this feed. Thanks for the input.
 
Location
CA, USA
409.110 might be of interest to you.

I looked it up and while it does provide the FLA, I am ultimately looking for MCA. I was also unsure if the MCA is 25% of the total unit or just the single motor, bu thankfully it was clarified above. Also, I am trying to figure this out because we do not have nameplate information at the moment. I am trying to properly size the feeder for this packaged unit.
 