How would we understand the "increase to the value marked on the controller" in the exception closing statement? What markings on controller is this referring to? In order to make sense to me it must mean the MCP in the listed controller can be increased. If the applications if technically lower in ratings and it is a listed controller it can be set to exceed the allowable 800% per that exception if not greater than 15A . Not finding much on this particular exception and the following is needing to be confirm.
Looking at using a UL listed controller with size 1 starter and 15A HMCP for a motor rated 1.5HP, 480V motor 3A FLC. The minimum setting is 45A on the magnetics of the 15A HMCP. The exception would seem to allow this but the statement to be increased to the value marked on the controller is confusing term. why not say breaker?
How would the FLA range for the HMCP 15A play into this exception which is 3.4-4.5A. it would seem NEC is taken exception to this factor in allowing for motors less then 8A?
Any insights to this exception and the meaning of that phrase would be much appreciated.
Looking at using a UL listed controller with size 1 starter and 15A HMCP for a motor rated 1.5HP, 480V motor 3A FLC. The minimum setting is 45A on the magnetics of the 15A HMCP. The exception would seem to allow this but the statement to be increased to the value marked on the controller is confusing term. why not say breaker?
How would the FLA range for the HMCP 15A play into this exception which is 3.4-4.5A. it would seem NEC is taken exception to this factor in allowing for motors less then 8A?
Any insights to this exception and the meaning of that phrase would be much appreciated.