Should article 430.52(B) applies to all types of motors?
or are there any exceptions that I have been missing.
I've seen design/installation that seems to be not following this, and approved by AHJs?
say for example, a 208V 3HP pool pump or a lift station where the branch breaker is sized around 20A.
Should it be sized based on its LRA? or is it because that these are small motors that LRA can be ignored?
Any thoughts?