NEC-430.53 Several Motors or Loads on One Branch Circuit

Status
Not open for further replies.

faresos

Senior Member
Hello All,

Question, I have two motors (1/3HP each) used for reel hose are connected to a 20A, 120V circuit. Each motor has a starter with overload protection. Reading 430.53 (A) it appears i'm not in compliance with #1 since 1/3HP (7.2FLA) exceeds the 6A. I always thought I can do it since until someone brought it to my attention. Any thoughts? Thanks in advance!

430.53(A) Not Over 1 Horsepower. Several motors, each not exceed-ing1 hp in rating, shall be permitted on a nominal 120-volt branch circuit protected at not over 20 amperes or a branch circuit of 1000 volts, nominal, or less, protected at not over 15 amperes, if all of the following conditions are met:
(1) The full-load rating of each motor does not exceed 6 amperes.
(2) The rating of the branch-circuit short-circuit and ground-faultprotective device marked on any of the controllers is not exceeded.
(3) Individual overload protection conforms to 430.32.
 

wwhitney

Senior Member
Location
Berkeley, CA
Occupation
Retired
Isn't the installation allowed under 430.53(B)? With a tabular FLC of 7.2A, the maximum allowable SC/GF OCPD for one motor is 250%*7.2 = 18A, which can be rounded up to 20A per 430.52(C)(1) Exception 1.

Cheers, Wayne
 