I scheduled 45A 2P circuit breakers for heat pumps. On heat pump submittal, MCA = 29.2A, Max Fuse Size = 45A. contractor panelboard submittal lists 50A 2P circuit breakers. When reading max fuse size, do I have to consider this to be maximum circuit breaker size. Can I allow a 50A c/b as long as it doesn't exceed 250% of compressor RLA? 440.22(C) refers to manufacturer's overlaod relay table for motor controllers so I'm interpreting this as not applying to nameplate data for a compressor. Am I correct?
For the contractors: do you find 35A, 45A sizes readily available?
For the contractors: do you find 35A, 45A sizes readily available?