electrical irishman
Member
In this code it state "Individual dry type transformers of more than 112 1/2 kVA rating shall be installed in a transformer room of fire-resistant construction. Unless specified otherwise in this article, the term fire resistant means a construction having a minimum fire rating of 1 hour. Exception No.1: transformers with Class 155 or higher insulation systems and separated from combustible material by a fire-resistant, heat-insulating....."
Okay my question is; is the code talking about the temperature rise or the system temperature that the transformer says it is rated for?
Okay my question is; is the code talking about the temperature rise or the system temperature that the transformer says it is rated for?