hello, i hope this isn't a re-post
i'm having trouble interpreting art. 450.3(b) note #3...
A transformer that comes with factory primary OCPD, may have a second primary OCPD installed as long as its not more then 6 times the rated primary current of the transformer, for transformers with 6% or less impedance. and if more than 6% - 10% impedance use 4 times the rated primary current.
is this the correct way to interpret this note?
-Thank you