mayanees
Senior Member
- Location
- Westminster, MD
- Occupation
- Electrical Engineer and Master Electrician
Does anyone have familiarity with the requirement for electric boilers above 1000 Volts to be powered with a solidly ground wye system?
495.71 Electrical Supply System.
Boilers shall be supplied only from a 3-phase, 4-wire solidly grounded wye system, or from isolating transformers arranged to provide such a system. Control circuit voltages shall not exceed 150 volts, shall be supplied from a grounded system, and shall have the controls in the ungrounded conductor.
Solidly grounded is defined as not being connected through a resistor or impedance.
I could understand that if the controls faulted each phase for heating, that there may need to be a minimum ground fault current available, but I could also see how the controls could function line-to-line to vary the heating process.
Thanks for any insight.
495.71 Electrical Supply System.
Boilers shall be supplied only from a 3-phase, 4-wire solidly grounded wye system, or from isolating transformers arranged to provide such a system. Control circuit voltages shall not exceed 150 volts, shall be supplied from a grounded system, and shall have the controls in the ungrounded conductor.
Solidly grounded is defined as not being connected through a resistor or impedance.
I could understand that if the controls faulted each phase for heating, that there may need to be a minimum ground fault current available, but I could also see how the controls could function line-to-line to vary the heating process.
Thanks for any insight.