I have avoided responding to this thread. In the absence of a general standard such as NFPA 496, I don’t believe the NEC provides sufficient instruction or references for designing or inspecting gas detection schemes except in very limited cases. The reference in FPN No. 2 relates to 500.7(K)(1) and (K)(2), FPN 3 relates to 500.7 (K)(3).
It must also be recognized that Section 500.7 lists protection techniques rather than Electrical Area Classification criteria listed in Section 500.5 and other locations, such as Articles 511-516.
In the case of Sub-section 500.7(K), it is a protection technique with very limited applications. It specifically permits “…electrical equipment for unclassified locations…” in 500(K)(2) only.
I was on CMP14 when this protection technique was first recognized. If the applications weren’t so limited at the time, I would have voted against it. If you read my affirmative statement, you will see that I made a point that using 500.7(K) does not alter the electrical area classification; it simply permits the use of electrical equipment for reduced classifications under very specific conditions. The original Panel Action directed users to base designs on currently recognized national standards. That was changed by the TCC. I still don’t believe the NEC provides adequate direction.
The problem is that API RP500 does permit altering the classification.
Having said that, RP500 Sub-section 6.5.2.e still must be interpreted in the whole context of the opening statement of Section 6.5.2 which immediately refers back to Section 6.5.1. Section 6.5.1 has much more comprehensive design criteria than the NEC.
However, Sub-section 6.5.2.e applies both to 6.5.1.a and 6.5.1.b. In the first case (6.5.1.a), the installation should have been suitable for Division 2 anyway. It permits the continued use of the installation – even where “…electrical equipment for unclassified locations…” is permitted in Division 2 as long as all the other requirements of 6.5.2 are met.
In the second case (6.5.1.b), some “…electrical equipment for unclassified locations…” is permitted in Division 2, some is not.
In either case (6.5.1.a and 6.5.1.b), if “…electrical equipment for unclassified locations…” is part of the installation, a shutdown is required.
This recognizes that a Division 2 installation is adequate for some Division 1 locations for a short time.