514.11 Circuit Disconnects.
(A) General. Each circuit leading to or through dispensing
equipment, including all associated power, communications,
data, and video circuits, and equipment for remote
pumping systems, shall be provided with a clearly identified
and readily accessible switch or other approved means,
located remote from the dispensing devices, to disconnect
simultaneously from the source of supply, all conductors of
the circuits, including the grounded conductor, if any.
Single-pole breakers utilizing handle ties shall not be
permitted.
...
(C) Unattended Self-Service Motor Fuel Dispensing Facilities.
Emergency controls as specified in 514.11 (A) shall
be installed at a location acceptable to the authority having
jurisdiction, but the control shall be more than 6 m (20 ft)
but less than 30 m (100 ft) from the dispensers. Additional
emergency controls shall be installed on each group of dispensers
or the outdoor equipment used to control the dispensers.
Emergency controls shall shut off all power to all
dispensing equipment at the station. Controls shall be
manually reset only in a manner approved by the authority
having jurisdiction.