NEC700.27 strict interpretation includes selective ground fault coordination throughout. However, NEC517.17(B) requires that ground fault SHALL NOT be provided on the load side of an ATS. This is due to the possiblity of nuisance tripping on source transfer downstream of the ATS.
How do you reconcile these two sections? The ATS is for the essential emergency circuit in a hospital.
Any thoughts?
Thank you!
How do you reconcile these two sections? The ATS is for the essential emergency circuit in a hospital.