tomgreen1000
Member
I am currently designing 4 story building with 8 tenants. It will have a 1200 amp 480/277 service, thus requiring GFPE on the service disconnect per 230-95. The intended use of this building is strictly doctors offices. It is not an ambulatory care center, it has no critical branch or emergency branch, it has no generator, there is no anesthesia, there is no dialysis, there is no surgery - just doctors offices. Portions of each tenant are exempt from 517 Part B per 517-10(b)(1). But the exam rooms are required to meet 517 Part B per 517-10(a).
So my question is, does 517-17 apply? My gut says yes. However, the building is classified as UBC occupancy class B (business) and not occupancy class I (healthcare). I checked with my local AHJ and they would NOT require 517-17 based on the occupancy rating. Usually this AHJ is very strict so I was a bit surprised. This job is not in my local AHJ and for a few reasons it is a bit sticky to contact the resident AHJ for the job location at this stage. Eventually I will contact the resident AHJ and it will be his/her final call, but in the meantime, please give me your opinion.
Thank you. Tom
So my question is, does 517-17 apply? My gut says yes. However, the building is classified as UBC occupancy class B (business) and not occupancy class I (healthcare). I checked with my local AHJ and they would NOT require 517-17 based on the occupancy rating. Usually this AHJ is very strict so I was a bit surprised. This job is not in my local AHJ and for a few reasons it is a bit sticky to contact the resident AHJ for the job location at this stage. Eventually I will contact the resident AHJ and it will be his/her final call, but in the meantime, please give me your opinion.
Thank you. Tom