Jon Lee

New member
Hello all, long time reader, first time posting.

I have a surgery center that I am inspecting, it is in the process of being expanded. It has two transfer switches, each one has a mixed/essential systems load. Due to the expansion the load on the essential systems exceeds the 150kVA allowed for a single transfer switch. My interpretation is that this does not comply with 517.30(B)(4), however the project engineer interprets it as complying, due to the fact that both transfer switches have a load NOT exceeding 150kVA. My position is that the entire essential systems load cannot exceed 150kVA, not just the load on a single transfer switch.

Thoughts?

Thank you for your time, this is a great forum.
 
Wow, the more I read this the less I understand it. :huh:



One transfer switch shall be permitted to serve one or more
branches or systems in a facility with a maximum demand
on the essential electrical system of 150 kVA.
 
Hello all, long time reader, first time posting.
My position is that the entire essential systems load cannot exceed 150kVA, not just the load on a single transfer switch.

Thoughts?

Thank you for your time, this is a great forum.

in a facility with a maximum demand
on the essential electrical system of 150 kVA.

I agree with you on that.
 
Hello all, long time reader, first time posting.

I have a surgery center that I am inspecting, it is in the process of being expanded. It has two transfer switches, each one has a mixed/essential systems load. Due to the expansion the load on the essential systems exceeds the 150kVA allowed for a single transfer switch. My interpretation is that this does not comply with 517.30(B)(4), however the project engineer interprets it as complying, due to the fact that both transfer switches have a load NOT exceeding 150kVA. My position is that the entire essential systems load cannot exceed 150kVA, not just the load on a single transfer switch.

Thoughts?

Thank you for your time, this is a great forum.

You are correct. Obviously this designer has never done any healthcare work to believe his own statement.
 
Hello all, long time reader, first time posting.

I have a surgery center that I am inspecting, it is in the process of being expanded. It has two transfer switches, each one has a mixed/essential systems load. Due to the expansion the load on the essential systems exceeds the 150kVA allowed for a single transfer switch. My interpretation is that this does not comply with 517.30(B)(4), however the project engineer interprets it as complying, due to the fact that both transfer switches have a load NOT exceeding 150kVA. My position is that the entire essential systems load cannot exceed 150kVA, not just the load on a single transfer switch.

Thoughts?

Thank you for your time, this is a great forum.

The ability to have 150 KVA or less applies to the use of a single transfer switch with regards to Essential Electrical Systems....over 150 KVA then multiple transformers are required.
 
I'm not sure exactly what loads are "mixed", but "optional" loads do not fall under the exception. If there are "optional loads", they would still require a separate transfer switch no matter what the essential load demand is.
 