Jon Lee
New member
- Location
- Las Vegas, Nevada USA
Hello all, long time reader, first time posting.
I have a surgery center that I am inspecting, it is in the process of being expanded. It has two transfer switches, each one has a mixed/essential systems load. Due to the expansion the load on the essential systems exceeds the 150kVA allowed for a single transfer switch. My interpretation is that this does not comply with 517.30(B)(4), however the project engineer interprets it as complying, due to the fact that both transfer switches have a load NOT exceeding 150kVA. My position is that the entire essential systems load cannot exceed 150kVA, not just the load on a single transfer switch.
Thoughts?
Thank you for your time, this is a great forum.
I have a surgery center that I am inspecting, it is in the process of being expanded. It has two transfer switches, each one has a mixed/essential systems load. Due to the expansion the load on the essential systems exceeds the 150kVA allowed for a single transfer switch. My interpretation is that this does not comply with 517.30(B)(4), however the project engineer interprets it as complying, due to the fact that both transfer switches have a load NOT exceeding 150kVA. My position is that the entire essential systems load cannot exceed 150kVA, not just the load on a single transfer switch.