I have the following questions on this code section and how it applies to Hospital Grade MC cable.
1. Can the hospital grade MC be used in branch circuits in patient care areas or does (1) limits you to hard pipe?
2. If the answer to the above question is "NO" than is it acceptable to hard pipe within a patient care area and set a j-box outside it (say in a corridor) and MC a homerun back to the panel?
3. Does this code section apply to feeders routed in "feeder type" MC cable? In other words if a feeder passes thru a patient care area to get to a panelboard, is hard pipe required as it is not a "branch circuit".
4. In the definitions of 517, how does patient care vancinity correlate with patient care area? Would lighting in a patient care area be exempt because its is above the 7'-6" height indicated in the definition of patient care vacinity?
Any input is greatly appreciated!