In NEC 517.34(B) for the electrical loads listed, when this code section says:
"(B) Equipment for Delayed Automatic or Manual Connection. The following equipment "shall be permitted" to be arranged for either delayed automatic or manual connection to the alternate power source"
By saying the statement above in this way it sounds like the electrical loads/equipment are allowed to be on the equipment branch but not required to be on the equipment branch.
I have some sterilizers in a hospital that were circuited to the normal branch of the electrical system and now I am debating with my colleagues if they are in violation of article 517.34(B)(6) which states that:
"Minimal electrically heated autoclaving equipment "shall be permitted" to be arranged for either automatic or manual connection to the alternate source."
Is 517.34(B) optional to comply with or do these loads have to be on the equipment branch?
"(B) Equipment for Delayed Automatic or Manual Connection. The following equipment "shall be permitted" to be arranged for either delayed automatic or manual connection to the alternate power source"
By saying the statement above in this way it sounds like the electrical loads/equipment are allowed to be on the equipment branch but not required to be on the equipment branch.
I have some sterilizers in a hospital that were circuited to the normal branch of the electrical system and now I am debating with my colleagues if they are in violation of article 517.34(B)(6) which states that:
"Minimal electrically heated autoclaving equipment "shall be permitted" to be arranged for either automatic or manual connection to the alternate source."
Is 517.34(B) optional to comply with or do these loads have to be on the equipment branch?