I have an Eye Doctor's Office that will perform eye surgery and I understand some of these rooms apply to NEC 517 and before I RFI this I want to be sure I have the correct questions and answers. My questions are:
1. Does an exam room apply to an eye doctor, not technically a Patient Care Area ? I take it Patient Care Area is defined with Exam rooms in is definition for General Care Areas but the engineer has designed the project with the exam rooms only being tamper resistant receptacles nec 406.11 which refers to 210.52 and my hand book refers this back to 517 pediatrics?
2. Does a Screening room apply for NEC 517? There is not a electric chair for a patient to sit in like in an exam room or a procedure room.
3. Does the lighting Branch Circuits have to be type Health Care Facility AC cable. The engineer has asked for Hospital Grade Red switches in the recovery room? I am not aware a manufacturer made a HG Switch?
517.13(b) exception #2: states Luminaires more than 7.5'ft above the floor and switches outside the patient care vicinity shall be permitted to be connected to an equipment grounding return path complying with 517.13(a) What about the light switch, it is below 7.5'ft?
Thank you for your time and help may God bless you and our Nation.
I cannot attach the drawing in question b/c it is larger than the allowed file size on this forum. If there is another way to post it let me know. Thanks
1. Does an exam room apply to an eye doctor, not technically a Patient Care Area ? I take it Patient Care Area is defined with Exam rooms in is definition for General Care Areas but the engineer has designed the project with the exam rooms only being tamper resistant receptacles nec 406.11 which refers to 210.52 and my hand book refers this back to 517 pediatrics?
2. Does a Screening room apply for NEC 517? There is not a electric chair for a patient to sit in like in an exam room or a procedure room.
3. Does the lighting Branch Circuits have to be type Health Care Facility AC cable. The engineer has asked for Hospital Grade Red switches in the recovery room? I am not aware a manufacturer made a HG Switch?
517.13(b) exception #2: states Luminaires more than 7.5'ft above the floor and switches outside the patient care vicinity shall be permitted to be connected to an equipment grounding return path complying with 517.13(a) What about the light switch, it is below 7.5'ft?
Thank you for your time and help may God bless you and our Nation.
I cannot attach the drawing in question b/c it is larger than the allowed file size on this forum. If there is another way to post it let me know. Thanks