hhsting
Senior Member
- Location
- Glen bunie, md, us
- Occupation
- Junior plan reviewer
Please see attached sketch. I have multi occupancy commercial building and one of the tenants space is ambulatory space which has multiple operation rooms, multiple procedure rooms, operation prep rooms and post surgery operation rooms.
The building has 2000A main SWBD with 2000A main fused disco with GFPE that feed to internal 2000A SWBD ATS whose emergency side (E) has NO generator connected in place. The internal ATS load side feed 6 feeder breakers in 2000A SWBD each with GFPE which feed 6 different tenant spaces and one of the feeder breakers feed ambulatory space 800A switchboard.
The 800A switchboard has feeder breakers which feed essential system for the ambulatory tenant space which has life safety ATS, critical system ATS and Equipment ATS. Their is emergency generator switchboard with emergency generator which backup essential system.
Please see attached sketch.
Questions:
1. The 2000A SWBD main fused disco has GFPE, all the SWBD feeder breakers has GFPE per NEC 2014 517.17(B). However, the feeder breakers and GFPE are load side of internal ATS in SWBD 2000A which does not have generator connected on emergency side and ATS is not necessary to be in place but hard to remove. The SWBD ATS 2000A feeds 6 tenants and one of them is ambulatory space which has essential system. NEC 2014 section 517.17(B) last paragraph says additional levels of ground fault protection shall not be installed on the load side of essential system transfer switch. In order to comply I am confused is the ATS 2000A SWBD essential transfer switch and like to know your opinion should the SWBD 2000A ATS be removed?
2. Assume the ambulatory space is fed from line side i.e service connection line side of 2000A SWBD fuse disco which is NOT the attached sketch shows. However just assume for a moment. I like to know all of your opinions would NEC 2014 Section 517.44(C) be used to argue and enforce that service connection from line side of 2000A SWBD fuse disco to ambulatory space SWBD INSTEAD of 2000A SWBD 800A feeder breaker feed to ambulatory space SWBD Shown in Attached sketch would cause less disruption or NEC 2014 NEC section 517.44(C) about something else?
The building has 2000A main SWBD with 2000A main fused disco with GFPE that feed to internal 2000A SWBD ATS whose emergency side (E) has NO generator connected in place. The internal ATS load side feed 6 feeder breakers in 2000A SWBD each with GFPE which feed 6 different tenant spaces and one of the feeder breakers feed ambulatory space 800A switchboard.
The 800A switchboard has feeder breakers which feed essential system for the ambulatory tenant space which has life safety ATS, critical system ATS and Equipment ATS. Their is emergency generator switchboard with emergency generator which backup essential system.
Please see attached sketch.
Questions:
1. The 2000A SWBD main fused disco has GFPE, all the SWBD feeder breakers has GFPE per NEC 2014 517.17(B). However, the feeder breakers and GFPE are load side of internal ATS in SWBD 2000A which does not have generator connected on emergency side and ATS is not necessary to be in place but hard to remove. The SWBD ATS 2000A feeds 6 tenants and one of them is ambulatory space which has essential system. NEC 2014 section 517.17(B) last paragraph says additional levels of ground fault protection shall not be installed on the load side of essential system transfer switch. In order to comply I am confused is the ATS 2000A SWBD essential transfer switch and like to know your opinion should the SWBD 2000A ATS be removed?
2. Assume the ambulatory space is fed from line side i.e service connection line side of 2000A SWBD fuse disco which is NOT the attached sketch shows. However just assume for a moment. I like to know all of your opinions would NEC 2014 Section 517.44(C) be used to argue and enforce that service connection from line side of 2000A SWBD fuse disco to ambulatory space SWBD INSTEAD of 2000A SWBD 800A feeder breaker feed to ambulatory space SWBD Shown in Attached sketch would cause less disruption or NEC 2014 NEC section 517.44(C) about something else?
Attachments
Last edited: