My inspector is telling me MC cable is not permitted in places of assembly. I don't see any exceptions in out state code either. Am I missing something?
cowboyjwc, Can you please give me a code reference. I assume your referring to the outside cable sheath? Thanks.
Check out 518.4(A) 2008 NEC. The addition of the requirement for the wiring method itself to qualify as an EGC is new to the NEC.
Chris
It also states the words 'or shall contain an insulated equipment grounding conductor'.