NEC 610.57 vs 110.26

Status
Not open for further replies.

DPW

Member
Location
FT. SMITH, AR
Can someone clarify the workspace clearance (30") for cranes is less than what is required in 110.26?

Need some help please.

Thanks in advance.
 

DPW

Member
Location
FT. SMITH, AR
NEC 610.57 vs 110.26

Does the workspace requirements of 610.57 less restrictive for cranes than 110.26 or is the requirements of Article 610 pertinent only for the restrictive space for cranes?
 

HoosierSparky

Senior Plans Examiner, MEP
Location
Scottsdale AZ
Occupation
Senior Plans Examiner
610.57 is restricted in its scope to cranes. Some cranes (gantry type) are usually accessed by boom/scissor lifts or ladders for their controls. Larger cranes usually have service walkways that are limited in width to the 2.5ft.
 