This is a link to a pretty good article, if I must say so myself.
http://www.csemag.com/article/CA6290839.html
http://www.csemag.com/article/CA6290839.html
The catch is to wire an IT room with the outlets fixed, conduits, strapped and limits on the use of flex under a raised floor as required under Chapter 1 through 4. The computer geeks I know won't go for having their future restricted by the permanent wiring methods used in most common electrical sites.Ron, that's a super article. The main thing that I learned is that an EPO button is not required. I guess that I always figured that computer rooms must have one.
No doubt about that.Originally posted by ron:
Funny, many think that if your compliant with 645, you can install any type of flex and not secure it. If you don't want to secure it, it must be listed for IT equipment,
That begs an obvious question for me, then. Is there some type of DP/IT rated cable that is available in bulk reel form for making field whips, much like people noncompliantly use SJT or SJO? If so, what's that stuff called?Originally posted by ron:
That's another struggle I have with facility operators, is that the cords they drop below the floor to plug into receptacles (or hardwire to j-boxes) are not DP rated.