17-67 Log #424 NEC-P17 Final Action: Accept in Principle
(680.7)
________________________________________________________
Submitter: Dan Leaf, Seneca, SC
Comment on Proposal No: 17-66
17-70 Log #455 NEC-P17 Final Action: Accept in Principle
(680.12)
________________________________________________________
TCC Action: The Technical Correlating Committee understands that the
final text of 680.12 includes both of the panel actions on Comments 17-70
and 17-71.
Submitter: Dan Leaf, Seneca, SC
Comment on Proposal No: 17-79
Recommendation: Accept proposal or revision as follows:
One or more approved means to simultaneously disconnect all ungrounded
conductors of the circuit shall be provided...(remainder unchanged).
Substantiation: Since the panel declined to accept a requirement for a switch
or circuit breaker, the means should be specifically required to be approved.
Simultaneous disconnection should be specified since literal wording, infers
that two or three individual disconnecting means may be used. Utilization
equipment includes signs within fountains which require a switch or circuit
breaker disconnecting means per 600.6. Since this rule is in Chapter 6, it may
be construed as amending other sections requiring simultaneous disconnect.
Panel Meeting Action: Accept in Principle
Revise 680.12 to read as follows:
680.12 Maintenance Disconnecting Means. One or more means to
simultaneously disconnect all ungrounded conductors shall be provided for
all utilization equipment other than lighting. Each means shall be readily
accessible and within sight from its equipment.
Panel Statement: The revised language more clearly presents the requirement
and meets the intent of the submitter.
Number Eligible to Vote: 11
Ballot Results: Affirmative: 10
Ballot Not Returned: 1 Gill, C.