Regarding NEC 682.30
NEC Article requires ?wiring within the scope of this article? to have an insulated equipment grounding conductor. Is the branch circuit from a residence to a GFCI receptacle that feeds a small aerator pump for a pond ?wiring within the scope of this article? or is it only on the load side of the disconnect or receptacle? Can a 12/2 uf be used for the branch circuit to the receptacle? The way I read 682.30 a uf would not be allowed. Is this a correct interpretation?
NEC Article requires ?wiring within the scope of this article? to have an insulated equipment grounding conductor. Is the branch circuit from a residence to a GFCI receptacle that feeds a small aerator pump for a pond ?wiring within the scope of this article? or is it only on the load side of the disconnect or receptacle? Can a 12/2 uf be used for the branch circuit to the receptacle? The way I read 682.30 a uf would not be allowed. Is this a correct interpretation?