PV Designer
Member
- Location
- California
- Occupation
- PV Designer
Solar carports are generally considered ground mounts, and not subject to the rapid shutdown requirements of NEC 690.12.
However, consider a carport with inverters mounted on its columns, the inverters are combined in a panel at the carport. The combined AC output conductors are then run underground to a nearby building, run up the exterior wall, over the rooftop, and down the opposite wall, to interconnect with the facility's main distribution panel in the the electrical room on the opposite side of the building from where the carport is located.
The rapid shutdown requirements of 690.12 clearly apply to the inverter AC output conductors on the building. However, the question is whether the AHJ will accept the AC disconnect as a sufficient RSID, since only the AC conductors are in question here. My reading of 2020 NEC 690.12(C) and (D) suggests that the AC disconnect in the interior electrical room where the utility meter and disconnect are located is a sufficiently code compliant, safe and effective RSID for the conductors in question, satisfying both the intention and the letter of the code.
My concern is that the AHJ may require RSID's on the DC side of the system, because these are specifically "listed" as RSID's.
What are your thoughts on this? Do you have any experience with similar situations? Obviously, I will not quote you in any legal disputes, but I am curious to know if my thinking is off, or on target. What do you think?
However, consider a carport with inverters mounted on its columns, the inverters are combined in a panel at the carport. The combined AC output conductors are then run underground to a nearby building, run up the exterior wall, over the rooftop, and down the opposite wall, to interconnect with the facility's main distribution panel in the the electrical room on the opposite side of the building from where the carport is located.
The rapid shutdown requirements of 690.12 clearly apply to the inverter AC output conductors on the building. However, the question is whether the AHJ will accept the AC disconnect as a sufficient RSID, since only the AC conductors are in question here. My reading of 2020 NEC 690.12(C) and (D) suggests that the AC disconnect in the interior electrical room where the utility meter and disconnect are located is a sufficiently code compliant, safe and effective RSID for the conductors in question, satisfying both the intention and the letter of the code.
My concern is that the AHJ may require RSID's on the DC side of the system, because these are specifically "listed" as RSID's.
What are your thoughts on this? Do you have any experience with similar situations? Obviously, I will not quote you in any legal disputes, but I am curious to know if my thinking is off, or on target. What do you think?