When designing PV systems smaller than 100kW, should NEC 2017 690.8(A)(1)(1) be followed by multiplying the 1.25 factor to the module Isc to check for MLPE and module level rapid shutdown device compatibility? I got myself confused since I've gotten different responses from various industrial professionals and articles.
1) For example, if my module Isc is 14A and my DC optimizer has a maximum short circuit input current of 15A, should I just calculate the adjusted module Isc based on temperature and irradiance (only slightly larger than 14A, thus still assuming 14A), and conclude that since 14A < 15A, the DC optimizer is compatible with the module? Or instead of doing the calculation, should I follow NEC 2017 690.8(A)(1)(1) and do 14A (module Isc shown on the datasheet with no adjustment applied) x 1.25 = 17.5A, 17.5A > 15A, thus the DC optimizer is not compatible with the module?
2) Does the same rule apply to module level rapid shutdown devices, which mostly have 15A max Isc input?
3) What about compatibility with string inverters without the use of MLPEs or module level rapid shutdown devices?
The points where I got confused are:
1) NEC defines PV source circuit current as module Isc x 1.25 per 690.8(A)(1)(1), and PV source circuit current is defined as the circuits between PV modules and from PV modules to a common connection point of the DC system. This definition of source circuit seems applicable to the case with MLPEs thus the max current should x1.25 based on the code. However, some MLPE manufacturers, such as Enphase and SolarEdge, indicate that the 1.25 factor does not need to be applied to the module Isc when checking for their device compatibility. Adjusted module Isc based on temperature can be directly referenced. Won't this conflict with the code?
2) Some string inverter manufacturers, such as SMA and Fronius, require the application of the 1.25 factor to module Isc when checking for inverter compatibility as written in their published whitepapers. Their max input Isc written on the inverter datasheets actually includes the 1.25 multiplier. So why does MLPE and string inverter differ in this requirement? Or does it depend on the manufacturer? Does this code only apply to a string of modules instead of individual module? And if so, why? Did I miss anything?
Sorry for the super long post since this conflict troubled me for a little while. I really appreciate it if someone can help clarify or advise. Thank you!
1) For example, if my module Isc is 14A and my DC optimizer has a maximum short circuit input current of 15A, should I just calculate the adjusted module Isc based on temperature and irradiance (only slightly larger than 14A, thus still assuming 14A), and conclude that since 14A < 15A, the DC optimizer is compatible with the module? Or instead of doing the calculation, should I follow NEC 2017 690.8(A)(1)(1) and do 14A (module Isc shown on the datasheet with no adjustment applied) x 1.25 = 17.5A, 17.5A > 15A, thus the DC optimizer is not compatible with the module?
2) Does the same rule apply to module level rapid shutdown devices, which mostly have 15A max Isc input?
3) What about compatibility with string inverters without the use of MLPEs or module level rapid shutdown devices?
The points where I got confused are:
1) NEC defines PV source circuit current as module Isc x 1.25 per 690.8(A)(1)(1), and PV source circuit current is defined as the circuits between PV modules and from PV modules to a common connection point of the DC system. This definition of source circuit seems applicable to the case with MLPEs thus the max current should x1.25 based on the code. However, some MLPE manufacturers, such as Enphase and SolarEdge, indicate that the 1.25 factor does not need to be applied to the module Isc when checking for their device compatibility. Adjusted module Isc based on temperature can be directly referenced. Won't this conflict with the code?
2) Some string inverter manufacturers, such as SMA and Fronius, require the application of the 1.25 factor to module Isc when checking for inverter compatibility as written in their published whitepapers. Their max input Isc written on the inverter datasheets actually includes the 1.25 multiplier. So why does MLPE and string inverter differ in this requirement? Or does it depend on the manufacturer? Does this code only apply to a string of modules instead of individual module? And if so, why? Did I miss anything?
Sorry for the super long post since this conflict troubled me for a little while. I really appreciate it if someone can help clarify or advise. Thank you!