hello guys i Have a question

In Nec 695.4 B a (2) which talk about the overcurrent protection device of the fire pump if the source is the standby generator .... Why we dont size the breaker to carry the locked rotor of the fire pump motor same as the breaker of the utility ?
 

ron

Senior Member
Do you mean 695.4(B)(2)(b) ?
This requirement correlates with 695.3(D)(1) covering the required capacity of an on-site standby generator. OCPDs supplied by an on-site standby generator are not required to be sized to carry the locked-rotor current (LRC) of the fire pump(s) indefinitely. The on-site standby generator is not limited to supplying only the fire pump. Where other pump room loads such as lights or fans are supplied, the generator must have sufficient capacity to instantaneously carry the entire load supplied. The OCPDs are not required to provide overload protection and are required to be sized per 430.62.
 

anas ibrahem

Member
Location
egypt
Occupation
Electrical engineer
i understood u but the requirement to sizing it not carry LRC same in multibuidling campus style complexes do you know the reason ?
 

Canton

Senior Member
Location
Virginia
Occupation
Electrician
i understood u but the requirement to sizing it not carry LRC same in multibuidling campus style complexes do you know the reason ?
Simply put…it’s a back up. If it had to meet the same requirements it would be way larger than needed
 