I was confused 695,6(B) indicates fire pump conductors on the load side of the final disconnect means and overcurrent devices...which I understood we should also count the conductor from fire pump controller to the fire pump motor?
I could see how that could be confusing. 695.6(B) talks about the conductors on the load side of the disconnecting means and ocpd permitted by 695.4(B).
The disconnecting means/ocpd permitted by 695.4(B) is to be installed between the power source and either the (1) fire pump controller, (2) fire pump transfer switch or (3) combination transfer switch/controller.
I would interpret the conductors in 695.6(B) to be only those from the disconnect to the controller, not those from the controller to pump.