lielec11
Senior Member
- Location
- Charlotte, NC
I just watched a webinar regarding NFPA 110, NEC 700-702, 708, and 517 as it relates to emergency and standby systems. A question came up in the Q&A portion that relates to NEC 700.10(B)(5) (2011 version) which states the following:
"Wiring from emergency source to supply and combination of emergency, legally required, or optional loads in accordance with (a), (b), (c), and (d);
a. From separate vertical switchboard sections, with or without a common, bus, or from individual disconnects mounted in separate enclosures
"
The presenters basically said that they have spoken to numerous AHJ's and said that since it is unpractical to provide separate vertical sections for every OCPD, they have no problem with approving the design as long as when they leave the switchboard they are separated.
I just wanted to spark a conversation and see everyone elses opinion. I have a job where we have a huge EMDB because of this section, and if I could get away without the separate vertical sections, and only separate AFTER the swbd, it could be much smaller.
"Wiring from emergency source to supply and combination of emergency, legally required, or optional loads in accordance with (a), (b), (c), and (d);
a. From separate vertical switchboard sections, with or without a common, bus, or from individual disconnects mounted in separate enclosures
"
The presenters basically said that they have spoken to numerous AHJ's and said that since it is unpractical to provide separate vertical sections for every OCPD, they have no problem with approving the design as long as when they leave the switchboard they are separated.
I just wanted to spark a conversation and see everyone elses opinion. I have a job where we have a huge EMDB because of this section, and if I could get away without the separate vertical sections, and only separate AFTER the swbd, it could be much smaller.